  #91  
Old 11-01-2012, 11:03 PM
Fairfax 944's Avatar
Fairfax 944 Fairfax 944 is offline
 
Join Date: Mar 2007
Location: Fairfax Station, VA
Posts: 983
Fairfax 944 has one HoF thread
Default

Quote:
Originally Posted by Jazzbass View Post
I can't believe for an instant that thing meets code.
They seem to imply that it does meet code:
http://www.interlockkit.com/warranty01.htm
Attached Images
 
__________________
Jim
1986 Porsche 944 Turbo

Last edited by Fairfax 944; 11-01-2012 at 11:37 PM.
Reply With Quote
  #92  
Old 11-01-2012, 11:15 PM
Jazzbass's Avatar
Jazzbass Jazzbass is offline
Site Admin
 
Join Date: Feb 2003
Location: Germantown, MD
Posts: 11,814
Jazzbass has eight HoF threadsJazzbass has eight HoF threadsJazzbass has eight HoF threadsJazzbass has eight HoF threadsJazzbass has eight HoF threadsJazzbass has eight HoF threadsJazzbass has eight HoF threads
Default

Ugh. Please use a transfer switch and wire your generator up correctly. Getting this stuff wrong has consequences. Not "oh no I blew a breaker" or even "oops, I fried my new generator" consequences, but "I killed a lineman" consequences.
__________________
Chris M
1985 911 Carrera with a couple cosmetic only mods
2006 E90 330i
1999 E46 328i
Reply With Quote
  #93  
Old 11-02-2012, 12:29 AM
tdatk's Avatar
tdatk tdatk is offline
Moonshine Tester
 
Join Date: Nov 2003
Location: Winchester, Va /Orlando,Fl/Tennessee
Posts: 2,927
tdatk has one HoF thread
Default

Quote:
Originally Posted by Jazzbass View Post
Ugh. Please use a transfer switch and wire your generator up correctly. Getting this stuff wrong has consequences. Not "oh no I blew a breaker" or even "oops, I fried my new generator" consequences, but "I killed a lineman" consequences.
Chris,
I rarely disagree with you on anything, but this arrangement, without a doubt meets NEC code. It has a mechanical interlock to prevent either circuit breaker from being on at the same time, I've seen much larger switch gear with essentially the same arrangement and they are just fine as long as they are physically intact. I've been an industrial electrician for over 25 years now so i can say with some authority that this is safe if installed as shown. Local code "may" require a transfer switch, but NEC does not.
__________________
Tim
05 Cayenne TT
03 M3 (sold)
82 911 SC (sold missed)
90 C2 (sold missed)
87 928 S4 (sold)
85.5 9 fofo (sold )
Reply With Quote
  #94  
Old 11-02-2012, 12:39 AM
Jazzbass's Avatar
Jazzbass Jazzbass is offline
Site Admin
 
Join Date: Feb 2003
Location: Germantown, MD
Posts: 11,814
Jazzbass has eight HoF threadsJazzbass has eight HoF threadsJazzbass has eight HoF threadsJazzbass has eight HoF threadsJazzbass has eight HoF threadsJazzbass has eight HoF threadsJazzbass has eight HoF threads
Default

Quote:
Originally Posted by tdatk View Post
Chris,
I rarely disagree with you on anything, but this arrangement, without a doubt meets NEC code. It has a mechanical interlock to prevent either circuit breaker from being on at the same time, I've seen much larger switch gear with essentially the same arrangement and they are just fine as long as they are physically intact. I've been an industrial electrician for over 25 years now so i can say with some authority that this is safe if installed as shown. Local code "may" require a transfer switch, but NEC does not.
Yeah, you're right. I know electrically this can be done correctly. It's the big red IF is the part that worries me. It just seems very hack-ish to me, that's all. When dealing with things that could unsuspectingly kill people, I always advise to pay the money and do it right.

To me its kind of like the harness bar vs roll bar debate for DEs. A harness bar is fine IF installed correctly, but when it comes to safety I'm a "no shortcuts" kind of person.
__________________
Chris M
1985 911 Carrera with a couple cosmetic only mods
2006 E90 330i
1999 E46 328i
Reply With Quote
  #95  
Old 11-02-2012, 12:58 AM
Eric S's Avatar
Eric S Eric S is offline
 
Join Date: Oct 2003
Posts: 1,081
Eric S
Default

Thanks for the ideas, links and recommendations; it appears that I should be able to install a safe, reasonably straightforward, and cosmetically satisfactory solution.

Eric


Quote:
Originally Posted by Vicegrip View Post
Yes there are. Unless you have a big azz genset you don't switch the entire house grid over and a Honda 2000 is not a big genset. y
You can get a tie in point installed in the basment and wires run to the service panel. In the basment you will have a box that has a big resessed plug and a row of switches. you run a power cable from the genset to the plug on the box and then flip the switches one at a time changing over from grid to gen set. Most folks myself included mount this device right next to the service panel but it can be placed elsewhere and the wires run in a fat conduit.
Quote:
Originally Posted by jbailey930 View Post
transfer switch something along the lines of this
http://www.homedepot.com/h_d1/N-5yc1...&storeId=10051
with surface mount works. you can size up the number of ckts and amps to suit your needs and gen.
Quote:
Originally Posted by SkankyFrank View Post
You don't have to mount it inside next to the main fuse panel, you can put it outside or in the garage and run the back up circuit wires from it to to the main panel. Running the circuit wires to the main panel can be much easier than running the power cord to the back up panel when it is next to the main panel because the circuit wires are much smaller and easier to "fish".
Quote:
Originally Posted by smdubovsky View Post
Yes. There are similar UL/NEC approved off-grid type setups where there is a sheet metal 'rocker' on two adjacent breakers. I'll try to find a pic. As long as you can mechanically prevent both from being on at the same time it should meet UL/NEC code. Now a home brew metal solution is *NOT* UL approved but you're within the letter of the law I think.

Edit: Square D transfer sw. UL/NEC approved: (there are other w/ the slider types approved.)
__________________
Previous:
2010 911 GT3
1993 911 RS America
1992 911 C2 Targa
Reply With Quote
  #96  
Old 11-02-2012, 08:07 AM
Fairfax 944's Avatar
Fairfax 944 Fairfax 944 is offline
 
Join Date: Mar 2007
Location: Fairfax Station, VA
Posts: 983
Fairfax 944 has one HoF thread
Default

Quote:
Originally Posted by Jazzbass View Post
I can't believe for an instant that thing meets code.
Keep in mind that there is another reason why this device won't meet code.

The latest version of the electrical code (adopted by Fairfax County) requires that your backup generator system be able to simultaneous power all circuit that are connected to the generator. Under the old code, it was legal for you to manually flip off circuit breakers and only power those that the generator could support.

So, if your electrical inspector is having a bad day or is being strict, you can't power your entire mail breaker panel with a 5Kw generator, but you must install a subpanel with limited breakers.
__________________
Jim
1986 Porsche 944 Turbo
Reply With Quote
  #97  
Old 11-02-2012, 08:47 AM
cmartin's Avatar
cmartin cmartin is offline
 
Join Date: Sep 2003
Location: Pasadena, MD
Posts: 7,577
cmartin
Default

A friend turned me on to this unit for a decent price.

http://www.amazon.com/dp/B00130GGRM

Only 3500/4400 watts but also 69db and $570. It should power my well pump, fridge, some lights.... as long as I dont turn them all on at the same time.
__________________
78 SC, the 'Red Car'
Reply With Quote
  #98  
Old 11-02-2012, 08:54 AM
smdubovsky's Avatar
smdubovsky smdubovsky is offline
 
Join Date: Mar 2004
Location: Silver Spring, MD
Posts: 5,281
smdubovsky has three HoF threadssmdubovsky has three HoF threadssmdubovsky has three HoF threads
Default

Quote:
Originally Posted by Fairfax 944 View Post
The latest version of the electrical code (adopted by Fairfax County) requires that your backup generator system be able to simultaneous power all circuit that are connected to the generator. Under the old code, it was legal for you to manually flip off circuit breakers and only power those that the generator could support.
IIRC, NEC covers the wiring not the removable generator. You don't need a genset there to pass inspection. A permanently wired unit is a different story.

Or is this some other local building code for fairfax? Has ffx adopted nec 2008 yet?
__________________
Stephen
www.salazar-racing.com
1970 914/6 - 3.0L GT
1983 911SC - 3.32L IROC
1984 930
2008 S2R1000, dirt bikes (some gas, some electric), Sherco trials bike
Sold: 2001 Boxster (hers), 2003 996tt x50 , SpecE30, 1996 E36M3 GTS2 racecar, 2015 Mustang GT
Reply With Quote
  #99  
Old 11-02-2012, 09:05 AM
Fairfax 944's Avatar
Fairfax 944 Fairfax 944 is offline
 
Join Date: Mar 2007
Location: Fairfax Station, VA
Posts: 983
Fairfax 944 has one HoF thread
Default

Quote:
Originally Posted by smdubovsky View Post
IIRC, NEC covers the wiring not the removable generator. You don't need a genset there to pass inspection. A permanently wired unit is a different story.

Or is this some other local building code for fairfax? Has ffx adopted nec 2008 yet?
Fairfax County has adopted NEC 2008. This load shedding issue was a concern for me when I installed a permanently attached propane generator. I didn't realize that this provision may not apply to a removable generator.
__________________
Jim
1986 Porsche 944 Turbo
Reply With Quote
  #100  
Old 11-02-2012, 10:09 AM
Trak Ratt's Avatar
Trak Ratt Trak Ratt is offline
Senior Curmudgeon
 
Join Date: Mar 2003
Location: Alexandria/Mt. Vernon, Va
Posts: 27,256
Trak Ratt has one HoF thread
Default

^ could prolly find it myself but a link would be nice. BTW no e-mail? I know you're busy but I wanted to make sure you had the right address.
__________________
David

I hope to arrive to my death, late, in love, and a little drunk!

Just because I don't care doesn't mean I don't understand... Homer Simpson

"That's what's keeping me out of F1.... Too much mental maturity...." N0tt0n

Some cause happiness wherever they go; others whenever they go.

CHAOS, PANIC, AND DISORDER my work here is done...

Live without pretending, Love without depending, Listen without defending, Speak without offending
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump